250.97 Bonding for Over 250 Volts
For circuits of over 250 volts to ground, the electrical conti-
nuity of metal raceways and cables with metal sheaths that
contain any conductor other than service conductors shall be
ensured by one or more of the methods specified for services
in 250.92(B), except for (B)(1).
Exception: Where oversized, concentric, or eccentric
knockouts are not encountered, or where a box or enclosure
with concentric or eccentric knockouts is listed to provide a
reliable bonding connection, the following methods shall be
permitted:
(1) Threadless couplings and connectors for cables with
metal sheaths
(2) Two locknuts, on rigid metal conduit or intermediate
metal conduit, one inside and one outside of boxes and
cabinets
(3) Fittings with shoulders that seat firmly against the box
or cabinet, such as electrical metallic tubing connec-
tors, flexible metal conduit connectors, and cable con-
nectors, with one locknut on the inside of boxes and
cabinets
(4) Listed fittings