I have equipment (roughly the size of a small refrigerator turned on its side, it is not a refrigerator however) that is cord and plug connected to a 20A 120V outlet. The cord enters the rear of the machine, and is routed inside the equipment approximately 3.5 feet and then lands inside a UL 467 grounding terminal block.
Someone is telling me that the NEC requires a separate chassis ground at the point the electric service enters the machine. I agree the equipment has to be connected to the equipment grounding conductor, which it is, but I do not see any where in article 250 that requires that this be done at the point cord enters the machine. Even if it did say this, what advantage is there to cutting my listed cord that early in the circuit, and then running MTW the rest of the way to the power and grounding terminal blocks.
Where in 250 does it say "at the point the electric service enters the machine"? I think my obligations under article 250 are to connect the machine to the equipment grounding conductor (near the supply TERMINALS and not the point of entry), and then the exception under 250.114...
Someone is telling me that the NEC requires a separate chassis ground at the point the electric service enters the machine. I agree the equipment has to be connected to the equipment grounding conductor, which it is, but I do not see any where in article 250 that requires that this be done at the point cord enters the machine. Even if it did say this, what advantage is there to cutting my listed cord that early in the circuit, and then running MTW the rest of the way to the power and grounding terminal blocks.
Where in 250 does it say "at the point the electric service enters the machine"? I think my obligations under article 250 are to connect the machine to the equipment grounding conductor (near the supply TERMINALS and not the point of entry), and then the exception under 250.114...