Check my calculation, Please.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
235 amp load, non-continuous. Conduit supplying the load is routed thru an area consistently at 100°F. Terminations are 75°
I see a 250kcmil Cu being required. THWN-2 Cu being utilized. VDrop is not an issue
Agree ? Disagree ?
 