A) Conduit fill derating does not apply to a JB,
B) Terminal temperatures do not apply to conduit.

For example, eight #12 THHN enter a JB, where some wire nuts are rated 75C. In the conduit, the 70% derating factor applies to the 90C column of table 310-16: 30A * 70% = 21A.

In the JB, use the 75C column of 310-16, 25 amps with no derating. So the ampacity of the circuit is 21A.

The point is, not to apply the 70% factor to the 75C column, which would only give 17.5 amps.
 
310.15(B) (2) and table (a) is adjustment factors for more than tree current-carrying conductors in a raceway or cable.


????????
 