I'm bidding a small industrial job and I want to check my calculations.
A motorized machine needs to be hooked up. It's 52 FLA, 3 phase, 460v. I don't have any other data on it such as motor type. It uses no motor starter according to the owner. It's being connected to a miniature bolt on breaker. The panel is 77 feet of conduit from the machine.
52 FLA so 6AWG THHN seems right.
Table C.1 says I can put 4 6AWG THHN in 3/4" EMT. I would run 1" for ease of pulling.
I looked at table 430.52 for breaker sizing and it says I can go a max of 250% of FLA so:
52 x 2.5 = 130. Next standard size up is 150. Next standard size down is 125 amp.
I haven't checked yet, but I'm not sure if a miniature 150 amp bolt-on breaker is available. I'm used to working with plug-on and the largest I see for those is 125 amp. Would a 125 amp breaker be sufficient?
A motorized machine needs to be hooked up. It's 52 FLA, 3 phase, 460v. I don't have any other data on it such as motor type. It uses no motor starter according to the owner. It's being connected to a miniature bolt on breaker. The panel is 77 feet of conduit from the machine.
52 FLA so 6AWG THHN seems right.
Table C.1 says I can put 4 6AWG THHN in 3/4" EMT. I would run 1" for ease of pulling.
I looked at table 430.52 for breaker sizing and it says I can go a max of 250% of FLA so:
52 x 2.5 = 130. Next standard size up is 150. Next standard size down is 125 amp.
I haven't checked yet, but I'm not sure if a miniature 150 amp bolt-on breaker is available. I'm used to working with plug-on and the largest I see for those is 125 amp. Would a 125 amp breaker be sufficient?