Check my motor sizing calcs pls

Status
Not open for further replies.

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I'm bidding a small industrial job and I want to check my calculations.

A motorized machine needs to be hooked up. It's 52 FLA, 3 phase, 460v. I don't have any other data on it such as motor type. It uses no motor starter according to the owner. It's being connected to a miniature bolt on breaker. The panel is 77 feet of conduit from the machine.

52 FLA so 6AWG THHN seems right.

Table C.1 says I can put 4 6AWG THHN in 3/4" EMT. I would run 1" for ease of pulling.

I looked at table 430.52 for breaker sizing and it says I can go a max of 250% of FLA so:

52 x 2.5 = 130. Next standard size up is 150. Next standard size down is 125 amp.

I haven't checked yet, but I'm not sure if a miniature 150 amp bolt-on breaker is available. I'm used to working with plug-on and the largest I see for those is 125 amp. Would a 125 amp breaker be sufficient?
 
Last edited:

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
If a machine has a rating of 52A then that is your circuit, all of the sizing has already been done by the manufacturer.

I think you are correct Dave, Your comment prompted me to take a much more in depth look at the specs I have for the machine. Even though it says 52 FLA, I think it really should say 52 amps. I don't see anywhere near 40 HP of motors in the thing.

If I was bidding, I would allow (3) 6 awg and a 60 amp breaker

I agree. Thanks.
 

zodiack

Member
Location
new york
Motor Calulations

Motor Calulations

I would think you would take the Full Load and have to add in 125 percent.
Look on the mane plate of running load if it has it. I not sure they would do that math for you Than your looking at a 70 amp breaker
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
O.p. said: "It uses no motor starter according to the owner"
If it is about DOL starting, the starting current may be 350 A.
However, according to NEC Art.430.52(C)(1) Exception 2(c) the maximum setting current for an inverse-time circuit breaker has to be not more than 400% [4*52=208 A].In these case see pos.(3) Instantaneous Trip Circuit Breaker.
The motor has to be provided with an overload device for 1.30*52=67.5 A-in my opinion.
 