I need to do a load calculation for a multifamily building I can't examine the actual stuff in. So I need reasonable defaults, even though
they can not practically be checked. How'd I do?
See any issues?

Do I derate the baseboard heaters once per unit THEN again for load diversity, as shown?

(The baseboard heating is part of what I'm unsure of (I wish it were watts per square foot of floor area making it easier to compute and less random))

Building 7Bedsft ²HeatLaundryCoolingRangeDisposalH2OD/WExtra§220.84 Load Calculation
12920--20.32VA84.67A
22920--20.32VA84.67A
32920-21.28VA88.67A
42920--20.32VA84.67A
52920-24.16VA100.67A
62920--20.32VA84.67A
72920--20.32VA84.67A
82920--21.28VA88.67A
Common-100-2-----240017.00VA70.83A
Constructed1986Raw sum185.32VA772.17A
After 43% demand factor for 8 units79.69VA332.03A
Net load with power managed EV (no change)79.69VA332.03A
LoadName-platederateCountLoad Diversity 220.84(B)
Heat960065%VABaseboard heaters, quantity less than 4345
Laundry9600VA40A electric dryer644
Cooling2400VAMinisplit843
Range8000VATypical range1132
Disposal2400VATypical disposal1241
H2O7200VA30A resistance tank water heater1440
Dishwasher3600VATypical dishwasher1639
Kitchen3000VAFixed value from 220.84(C)(2)1838
 
Do I derate the baseboard heaters once per unit THEN again for load diversity, as shown?
No. 220.84 is self-contained and nothing in 220 Part III applies. 220.84 has no reference to a 65% factor for heating. You put in the full nameplate rating of all heating as specified in 220.84(C)(5), unless the cooling load is higher.

It is interesting that 220.84(C)(3) and (4) specifically refer to the nameplate, while (5) does not. And Part II of 220 still applies. So if, for example, 220.14 had special rules for heating, those would still apply to determine the heating "load". But it doesn't, heating would fall under the 220.14(A) catchall which just refers to the "ampere rating".

Note that for cooling (or heat pump heating), 220.14(C) does refer you to 430/440 for motor loads, so the load would be the nameplate MCA.

No opinion on any of your default values, as I have no applicable experience.

Cheers, Wayne
 
No. 220.84 is self-contained and nothing in 220 Part III applies. 220.84 has no reference to a 65% factor for heating. You put in the full nameplate rating of all heating as specified in 220.84(C)(5), unless the cooling load is higher.
That's what's getting me
220.84 (C)(5) The larger of the air-conditioning load or the fixed electric space-heating load

It does not say "nameplate" it says "load". So what's the load?

That's where I dragged out:
65 percent of the nameplate rating(s) of electric space-heating if less than four separately controlled units.
40 percent of the nameplate rating(s) of electric space-heating if four or more separately controlled units."

----------------------------------------------

I updated the dyer to 7680 VA ( 80% of the 40A breaker, allowing a commercial 32A machine)>
Building 7Bedsft ²HeatLaundryCoolingRangeDisposalH2OD/WExtra§220.84 Load Calculation
12920--20.03kVA83.47A
22920--20.03kVA83.47A
32920--20.03kVA83.47A
42920--20.03kVA83.47A
52920--20.03kVA83.47A
62920--20.03kVA83.47A
72920--20.03kVA83.47A
82920--20.99kVA87.47A
House-100-2-----240015.46kVA64.43A
736.17
ConstructedRawsum176.68kVA736.17A
1986After43% diversityfactor for 8 unit75.97kVA316.55A
Net w/EV loadmanagement75.97kVA360.00A
Net w/EV communication fail (add 6 unmanaged chargers at 1.4kW)84.61kVA352.55A
LoadName-platederateCountLoad Diversity 220.84(B)
Heat7680100%VABaseboard heaters, separate controls, quantity less than 4345
Laundry7680100%VA40A circuits 32A Max Dryers, demand factor per 220.54644
Cooling1920VAMinisplit 240V at 16A843
Range8000VATypical range, Table 220.551132
Disposal1440VATypical disposal1241
H2O5760VA30A resistance tank water heater at 80%1440
Dishwasher1440VATypical dishwasher1639
Kitchen3000VAFixed value from 220.84(C)(2)1838
 
That's what's getting me
220.84 (C)(5) The larger of the air-conditioning load or the fixed electric space-heating load

It does not say "nameplate" it says "load". So what's the load?

That's where I dragged out:
65 percent of the nameplate rating(s) of electric space-heating if less than four separately controlled units.
40 percent of the nameplate rating(s) of electric space-heating if four or more separately controlled units."
OK, but that language is from 220.82. Nothing in 220.84 references 220.82.

The first sentence of 220.84 says in part "in accordance with Table 220.84(B) instead of Part III of this article." It's basically saying 220.84 is self-contained.

I don't have an explanation for the difference in language between 220.84(C)(3)/(4) and (5), but I don't think it's significant.

Cheers, Wayne
 