I need some oversight on my load calculation. Here is what I came up with.
3400 sq ft @ 3va = 10200VA
4 (assuming) SABC @ 1500VA = 6000VA
2 Laundry circuits @ 1500VA = 3000VA
Double oven @ 9600VA =9600VA
2 Dish washers @ 1200VA = 2400VA
2 Dryers @ 5000VA = 10000VA
Total General Load = 41200VA
First 10000 kVA @100%
40100 - 10000 = 31200VA
31200 x 40% = 12480VA
12480VA + 10000 = 22480VA
20400VA HVAC load (largest of AC vs Heat on 2 units)
20400VA + 22480VA = 42880VA
42880VA ÷ 240V = 179A
If this is correct then I could use a 200A service.