Here is a dock disconnect fed from a breaker at the condo
This is the J box were they spliced the neutral to feed the dock and then to disconnect the black spot is from the a poorly taped lug
"250.6(C) Temporary Currents Not Classified as Ojectionable Currents.
Temporary currents resulting from accidental conditions, such as ground faults, shall not be classified as objectionable current for the purposes specified in 250.6(A) and (B)."
"250.6(C) Temporary Currents Not Classified as Ojectionable Currents.
Temporary currents resulting from accidental conditions, such as ground faults, shall not be classified as objectionable current for the purposes specified in 250.6(A) and (B)."
Okay....maybe I misunderstood yours. You made this comment regarding my original comment. What did you mean?
A neutral connection to an equipment grounding conductor is not a Ground Fault, it is Objectional Current.
From the arc on the cover as pictured, I saw a ground fault condition.
Neutral-ground connections are considered as Objectional Current, I agree.
im confused. Why isnt there a neutral leaving the breaker enclosure?
im confused. Why isnt there a neutral leaving the breaker enclosure?
"Short Answer"
If this is a picture of service equipment.........a grounded conductor is required to be brought in with the supply.
On the Load side it appears an equipment grounding conductor of the wire type is run with the ungrounded conductors to the load.(in this pic, hard to tell but looks like EGC is too small)
A neutral is not necessary if the load does not require one......Maybe its feeding a 240 volt 2 wire something?
You are sure the neutral was arcing to the cover?
What happend to the days when you could jam all those splices in there and use a furring strip to keep them away from the cover.I have often worried about the sharp ends of split bolts poking thru scotch pad and tape over time, just like it appears in the picture.
I have often worried about the sharp ends of split bolts poking thru scotch pad and tape over time, just like it appears in the picture.
Here is a dock disconnect fed from a breaker at the condo
This is the J box were they spliced the neutral to feed the dock and then to disconnect the black spot is from the a poorly taped lug
This is the J box were they spliced the neutral to feed the dock and then to disconnect the black spot is from the a poorly taped lug