@ngeLCD
Member
- Location
- Pennsylvania
- Occupation
- Commercial real estate develoment/construction, avid DIY'er
A pool is being constructed at my house, and the electrical sub recently completed their task. I'm in Pennsylvania which is under NEC 2014 I believe. In reviewing their work, I had some questions, and was hoping to confirm my suspicions. Two 50A two pole breakers were installed in my main panel. One for the heat pump, and one for the pool control panel which in turn has the other pool equipment wired to it. The heat pump circuit is 240V only, and the other pool circuit is 120/240V. Accordingly two hots were installed for the heat pump circuit, two hots and a neutral for the other pool circuit, and a shared ground. All of the conductors installed as well as the shared ground are 8awg copper thhn. All 6 wires (5 current carrying, 1 ground) are in a single 1" PVC conduit and the run for both circuits is approximately 95' one way. My concern is with the size of the conductors that were installed. My read of the situation is that while Table 310.15(B)(16) rates the 8awg conductors at 55A, Table 310.15(B)(3)(a) requires an 80% adjustment factor due to 5 current carrying conductors sharing a conduit. Therefore the five current carrying conductors should be upsized to 6awg. In addition I have a voltage drop concern on the 120/240V circuit, but that's besides the point if my first concern is valid. I wanted to ask if my read is correct, or if I'm missing something that would make 8awg conductors acceptable in this application. Thanks!