I'm bidding a job that requires and I quote.
"Check ground system with "earth megger". Furnish the test result to owner and engineer. The readings shall be 25 ohms or less."
This is a 20 story building. I'm only to install a sub panel fed by a main panel for this floor which is fed by a bus duct. I can understand checking my work to the floor panel, but I don't see how I can include in my bid a guarantee that the existing grounding system is 25 ohms or less.
How would I even check the whole system? I assume the building steel and incoming water line are probably the grounds for the building. There's concrete and pavement all around the building with the exception of a small flower garden that may even have a concrete bottom.