It seems to give you only a local area of low resistance.
"One can visualize the effective radius, or earth shell, of a ground rod as a
buried hemisphere with a radius equal to the rod length. If two rods are spaced closer than their
length, the hemispheres overlap. The resistance will be less than that of a single rod but will not
be one half the resistance of a single rod: it will be more.
Conductive-cement rods and electrolytic rods have larger earth shells and should be spaced
farther apart, at least twice the rod length. "
So your rod system is isolated from the wider area more than rods buried in more conductive soil.