Chicago Electric Code

Status
Not open for further replies.

frd4gfa

Member
Location
Somerset, NJ
I have been told that I can't use 277V lighting fixtures and/or wall switches mounted less than 8'0" AFF in Chicago. I am not able to find this in the Chicago Electric Code. Does anyone know what the code reference for this issue is.
 
I'm not from the Chicago area so I'm not awear of the "Chicago Code" but this is a NEC violation Art,404.8(A) - Switches shall not be more then 6'7" above AFF.
 
No, the issue isn't related to the maximum height of the switch, per se, but rather the minimum height allowed (AFF), in Chicago, of a device that is part of a 277V circuit. So I am looking for someone who might have some experience with the Chicago Electric Code. Thank you for your reply.
 
frd4gfa said:
I have been told that I can't use 277V lighting fixtures and/or wall switches mounted less than 8'0" AFF in Chicago. I am not able to find this in the Chicago Electric Code. Does anyone know what the code reference for this issue is.

Do you have a copy to use as reference?
 
From the Chicago Code Book

18-27-210.6. Branch Circuit Voltage Limitations.
(a) Occupancy Limitations. In dwelling units and guest rooms of hotels, motels, and similar occupancies, the voltage shall not
exceed 120 volts, nominal, between conductors that supply the terminals of:
(1) Lighting fixtures;
(2) Cord- and plug- connected loads of less than 1440 volt-amperes nominal.
(b) 120 volts Between Conductors. Circuits not exceeding 120 volts nominal, between conductors shall be permitted to supply the
following:
(1) The terminals of medium-base screw-shell lampholders or lampholders of other types applied within their voltage ratings;
(2) Auxiliary equipment of electric discharge lamps;
(3) Cord and plug connected or permanently connected utilization equipment.
(c) 277 Volts to Ground. Provided the premises is under the supervision of a Supervising Electrician employed by the company or
by a contract with a registered electrical contractor, circuits exceeding 120 volts, nominal, between conductors and not exceeding 277
volts, nominal, to ground shall be permitted to supply the following equipment:

(1) Lighting fixtures equipped with mogul-base screw shell lampholders or with lampholders other than the screw shell-type applied
within their voltage ratings provided:
(a) The light fixtures are installed at least 8 ft above the floor;
(b) The light fixtures have a conspicuous warning notice within the wiring compartment indicating the circuit voltage;
(c) The light fixtures are permanently installed;
(d) Switching is by low-voltage remote control relays or by circuit breakers within the branch circuit distribution panel;
(e) Circuit interrupting toggle switches are not used;
(f) The lighting fixtures do not have integral switches.

(2) Auxiliary equipment of electric discharge lamps provided:
(a) The light fixtures are installed at least 8 ft above the floor;
(b) The light fixtures have a conspicuous warning notice within the wiring compartment indicating the circuit voltage;
(c) The light fixtures are permanently installed;
(d) Switching is by low-voltage remote control relays or by circuit breakers within the branch circuit distribution panel;
(e) Circuit interrupting toggle switches are not used;
(f) The lighting fixtures does not have integral switches.

(3) Permanently installed and connected utilization equipment provided:
(a) The equipment has a conspicuous warning notice within the wiring compartment indicating the circuit voltage;
(b) The equipment is permanently installed;
(c) Switching is by low-voltage remote control relays or by circuit breakers within the branch circuit distribution panel;
(e) Circuit interrupting toggle switches are not used.
(f) Kitchen equipment is not installed at voltages of more than 150 volts to ground.
(d) 600 Volts Between Conductors. Provided the premises is under the supervision of a Supervising Electrician employed by the
 
Last edited:
18-27-380.14. Rating and Use of Snap Switches.
Snap switches shall be used within their ratings and as indicated in (a) through (d) of this section.
FPN No. 1: For switches on signs and outline lighting, see Section 18-27-600.6.
FPN No. 2: For switches controlling motors, see Sections 18-27-430.83, 430.109, and 430.110.
(a) Alternating Current General-Use Snap Switch. A form of general-use snap switch suitable only for use on alternating-current
circuits for controlling the following:
(1) Resistive and inductive loads, including electric-discharge lamps, not exceeding the ampere rating of the switch at the voltage
involved;
(2) Tungsten-filament lamp loads not exceeding the ampere rating of the switch at 120 volts;
(3) Motor loads not exceeding 80 percent of the ampere rating of the switch at its rated voltage.
(b) Alternating-Current or Direct-Current General-Use Snap Switch. A form of general-use snap switch suitable for use on
either ac or dc circuits for controlling the following:
(1) Resistive loads not exceeding the ampere rating of the switch at the voltage applied;
(2) Inductive loads not exceeding 50 percent of the ampere rating of the switch at the applied voltage. Switches rated in
horsepower are suitable for controlling motor loads within their rating at the voltage applied;
(3) Tungsten-filament lamp loads not exceeding the ampere rating of the switch at the applied voltage if T-rated.
(c) CO/ALR Snap Switches. Snap switches rated 20 amperes or less directly connected to aluminum conductors shall be listed and
marked CO/ALR.
(d) Voltage. Snap toggle switches shall not be used for the control of 277/480 volt circuits.
 
Thanks Russ...

Thanks Russ...

Yeah, I do have the latest edition of the Chicago code but having one of those geriatric moments, I guess, I have been looking for this reference in 18-27-210.6, (c); 277 Volts to Ground and just couldn't find it.
I appreciate your response.
 
BryanMD said:
The low voltage switching sorta makes sense but must be a PITA.
The 8 foot limit sounds more like a 517 issue (being misinterpreted).
In any case, is 277 ever supplied to a residence?


The first part of the Chicago code version of 210.6 kinda rules that out for the average house.
If there are any, I've never heard of them.
 