I have a project that the engineer is calling for liquid tight flexible conduit to be used to connect fan motors to conduit on the inside of air handling units that supply various areas within a hospital. We are saying that this is a violation of NEC 300.22(b) and City of Chicago code 18-27-351.4.(b).11 that state "Liquidtight flexible metal conduit which has an outer jacket of nonmetallic material shall not be used as a raceway in environmental air handling ducts or spaces (plenums)."
One would thing that, especially in a hospital environment, you would not want to risk the possibility of releasing toxic PVC fumes into patient/OR rooms in the event of a fire.
I realize that the NEC has no bearing in Chicago so I'm trying to get a feel from others that have worked more in Chicago than I have.
One would thing that, especially in a hospital environment, you would not want to risk the possibility of releasing toxic PVC fumes into patient/OR rooms in the event of a fire.
I realize that the NEC has no bearing in Chicago so I'm trying to get a feel from others that have worked more in Chicago than I have.