I am a building owner in Chicago. I am told by am electrician that I have to register a contract for them to be inspector of record with the Electrical Bureau fo the Coty of Chicago.
OK no problem.
Then they tell me I have to pay for WEEKLY inspections. I have a hard tie believing that. They tell me I need this because of 18-27-210.6 "Branch Circuit Voltage Limitations" See copied below.
Could this be true? I see know where that it says weekly inspections. I have called Chicago and do not get a response.
Thanks
(c) 277 Volts to Ground. Provided the premises is under the supervision of a Supervising Electrician employed by the company or by a contract with a registered electrical contractor, circuits exceeding 120 volts, nominal, between conductors and not exceeding 277 volts, nominal, to ground shall be permitted to supply the following equipment:
(1) Lighting fixtures equipped with mogul- base screw shell lampholders or with lampholders other than the screw shell-type applied within their voltage ratings provided:
(a) The light fixtures are installed at least 8 ft above the floor;
(b) The light fixtures have a conspicuous warning notice within the wiring compartment indicating the circuit voltage;
(c) The light fixtures are permanently installed;
(d) Switching is by low-voltage remote control relays or by circuit breakers within the branch circuit distribution panel;
(e) Circuit interrupting toggle switches are not used;
(F) The lighting fixtures do not have integral switches.
(2) Auxiliary equipment of electric discharge lamps provided:
(f) The lighting fixtures does not have integral switches.
(3) Permanently installed and connected utilization equipment provided:
(a) The equipment has a conspicuous warning notice within the wiring compartment indicating the circuit voltage;
(b) The equipment is permanently installed;
(c) Switching is by low-voltage remote control relays or by circuit breakers within the branch circuit distribution panel;
(e) Circuit interrupting toggle switches are not used.
(f) Kitchen equipment is not installed at voltages of more than 150 volts to ground.
OK no problem.
Thanks