WHAT PART, ARTICLE TALKS ABOUT CHILD-PROOF RECEPTACLES IN DEWELLINGs.

I NEED TO KNOW WHERE IN THE HOUSE POWER OUTLETS REQUIRED TO BE CH. PR..

THANK YOU
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Basically everywhere.
You should not be even stocking anything else for residential application as replacemets are a requirement also.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
hI

WHAT PART, ARTICLE TALKS ABOUT CHILD-PROOF RECEPTACLES IN DEWELLINGs.

I NEED TO KNOW WHERE IN THE HOUSE POWER OUTLETS REQUIRED TO BE CH. PR..

THANK YOU

406.11 Tamper-Resistant Receptacles in Dwelling Units. Changed from 2005


?
spacer.gif
406.11: Added a requirement for tamper-resistant 15- and 20-ampere, 125 volt receptacles in dwelling units.


In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
No such thing as child proof. As soon as you think you have it, along comes a smarter child.

Sorta like idiot proof; as soon as you have it, along comes a better idiot.:jawdrop:
 

kwired

Electron manager
Location
NE Nebraska
This was also something that was added in 2008 NEC if I remember correctly, so unless you were in a place that is behind on adopting current editions or doing very little for residential installations since then you probably should have found out about it some time ago.;)
 