ItsHot said:
Can anyone provide any information on the new requirements for child tamper proof receptacles. Thank You

406.11 Tamper-Resistant Receptacles in Dwelling Units. In all areas specified in 210.52, all 125-volts, 15 and 20 ampere receptacles shall be listed tamper-resistant receptacles.
 