I would get very accurate actual motor amperage readings during runtime.
And you want to make sure your motor is thermally protected via internal means, or external overload detection.
If you find the actual motor amperage exceeding nameplate readings, the easiest way to reduce is to throttle back on the intake (suction line). Many times there is a 90deg ball valve on the inlet of the pump for servicing purposes. You can close this valve a few degrees while watching your ampmeter. (Don't close the valve so much to cavitate or starve the pump however). If this provides a solution, you will want to mechanically limit the stroke of the valve permanently or post signage, sot that subsequent service technicians don't open the valve fully in the future.
Also, agree with other responses, IR temperature measurment can only be taken if you are trained to do so. The "casual" IR measurment is good for relative comparisons, as an example checking the terminal lugs of a motor starter or circuitbreaker, and comparing L1 vs L2 vs L3.
Using IR to actually quantify a temperature you must be aware of Emmisivity settings on your IR instrument. Emmisivity is a function of the COLOR of the object that you are trying to obtain the IR temperature reading from.