A bit long winded, but I could use some help/insight.
We have a site with several Chillers’ they have reduced voltage starting.
One of the chillers keeps tripping the feeder circuit breaker on ground fault at start up.
Chiller is a 3 phase 480 VAC
Once started the chiller runs fine.
Here is what we have.
800 amp GE circuit breaker with a MicroVersa Trip PM Trip Unit, with a 300 amp rating plug
There is a neutral CT that is not utilized, though it is connected to the circuit breaker.
Long Time 6 delay 24
Instantaneous 7
Short Time at 9 delay 1
Ground Fault .2 and delay 1
The circuit breaker was primary injection tested last year
Secondary injection tested last week and tested satisfactorily
The GFP was primary injection tested last week and tested satisfactorily
The GFP pickup is based on the circuit breaker sensors so ground fault pickup is 160 amps.
We utilized a high speed recorder to monitor voltage and current, we monitored A, B, and C phase currents plus a single CT was placed around all three phase conductors and a separate CT was placed on the EGC.
In our test we did not get a trip of the feeder circuit breaker, this is what we did see.
AT START UP
A, B, C inrush currents in excessive of 1,100 amps, (due to limitations of the CT’s we could not capture the exact inrush currents)
The zero sequence CT-150 amps
The EGC CT-135 amps (it is not feasible to capture true ground current as there are multiple ground paths).
Prior to us arriving on site the building electricians swapped circuit breakers between chillers and had the same issue with this chiller with a different circuit breaker.
This chiller has been on line for about 10 years and the issue occurred a few times, but in July the tripping on GFP became a regular occurrence.
The chiller was meggered at 1000 VDC and the readings were above 2000, Megohms (by others)
The feeder was meggered with similar results.
We could not monitor the other chillers at this site as they were in use, I’d like to see if there is a similar issue with other units.
With transformers we have had ground fault tripping issues when the GFP relay was set low, the design engineers made changes in the coordination study to overcome this issue.
Is it reasonable to assume that there would be some zero sequence current on a 3 phase high inrush load on start up?
Or is my assumption incorrect?
Is it possible to have induced current on the EGC during high inrush start ups? (Is this what I am seeing?)
This chiller operated with minimal issues for 10 years, could this issue have been existing all along and only gotten worse due to aging of the motor, bearings or something with the chiller that added additional load during startup?
We have a site with several Chillers’ they have reduced voltage starting.
One of the chillers keeps tripping the feeder circuit breaker on ground fault at start up.
Chiller is a 3 phase 480 VAC
Once started the chiller runs fine.
Here is what we have.
800 amp GE circuit breaker with a MicroVersa Trip PM Trip Unit, with a 300 amp rating plug
There is a neutral CT that is not utilized, though it is connected to the circuit breaker.
Long Time 6 delay 24
Instantaneous 7
Short Time at 9 delay 1
Ground Fault .2 and delay 1
The circuit breaker was primary injection tested last year
Secondary injection tested last week and tested satisfactorily
The GFP was primary injection tested last week and tested satisfactorily
The GFP pickup is based on the circuit breaker sensors so ground fault pickup is 160 amps.
We utilized a high speed recorder to monitor voltage and current, we monitored A, B, and C phase currents plus a single CT was placed around all three phase conductors and a separate CT was placed on the EGC.
In our test we did not get a trip of the feeder circuit breaker, this is what we did see.
AT START UP
A, B, C inrush currents in excessive of 1,100 amps, (due to limitations of the CT’s we could not capture the exact inrush currents)
The zero sequence CT-150 amps
The EGC CT-135 amps (it is not feasible to capture true ground current as there are multiple ground paths).
Prior to us arriving on site the building electricians swapped circuit breakers between chillers and had the same issue with this chiller with a different circuit breaker.
This chiller has been on line for about 10 years and the issue occurred a few times, but in July the tripping on GFP became a regular occurrence.
The chiller was meggered at 1000 VDC and the readings were above 2000, Megohms (by others)
The feeder was meggered with similar results.
We could not monitor the other chillers at this site as they were in use, I’d like to see if there is a similar issue with other units.
With transformers we have had ground fault tripping issues when the GFP relay was set low, the design engineers made changes in the coordination study to overcome this issue.
Is it reasonable to assume that there would be some zero sequence current on a 3 phase high inrush load on start up?
Or is my assumption incorrect?
Is it possible to have induced current on the EGC during high inrush start ups? (Is this what I am seeing?)
This chiller operated with minimal issues for 10 years, could this issue have been existing all along and only gotten worse due to aging of the motor, bearings or something with the chiller that added additional load during startup?