Chiller module disconnect switch within sight

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
We will be installing chiller modules and they have an internal disconnect switch as seen below circled in blue:

1710879746111.png

Does this satisfy code saying that we need a disconnect switch within sight of the equipment? Or do I need another disconnect switch next to it external of the equipment?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As far as the NEC is concerned it appears that the unit switch satisfies the disconnect requirement.
 
Top