Christmas light show
WSB123
I am currently pricing an estimate to provide the electrical infrastructure for a lighting company to install Christmas lighting in a local park. The lighting company has not provided any detailed information on load requirements. They asked how much load could they put on a 20 amp / 120 volt circuit and I told them 16 amps with a continuous load. They have requested 28 quad receptacle locations each supplied by two 20 amp circuits.
In calculating my load, are there any demand factors I need to figure for sizing the service, or do I assume 16 amps continuously for my calculation? I just am not familiar with the actual current draws for such lighting events and apparently 16 amps per circuit is the only information the lighting installers can provide. The EMC has 480v service nearby so I will be setting a couple of padmount transformers and panels.
Thank you in advance for your input.
I would assume 16 amps per circuit.
Yes, each location would have (2) 20 amp circuits. I will assume the 16 amps in my calculations. Thank you, both, for your input
I would say they have no idea what they're doing. 28 locations * 2 circuits * 1920va/circuit = 107.6 KVA, that is not realistic unless maybe the site is a huge building covered with incandescent lights and a lot of non-lighting loads. It would also cost a lot.
For a local park, I'd guess that 4-6 20 amp circuits should be sufficient for LED lights and all but the most complex setups.