Length of cord between the GFCI device and the lights. Too much cable means the return current takes too long to “return” to the GFCI and it trips.
Not really.Length of cord between the GFCI device and the lights. Too much cable means the return current takes too long to “return” to the GFCI and it trips.
Cords connected laying on the ground without any protection to keep water from entering those connections?
It could be a 2 wire.This is what I'm thinking; if the cord is a 3 conductor cord where the current could be leaking to ground.
It could be a 2 wire.
Lay a two wire GFCI protect cord in the grass, plug another into it and continue on to several snowflakes or Angels in the yard. Run the sprinklers on it or wait for a heavy foggy, maybe drizzling day. Let me know how things turn out.Highly unlikely
Lay a two wire GFCI protect cord in the grass, plug another into it and continue on to several snowflakes or Angels in the yard. Run the sprinklers on it or wait for a heavy foggy, maybe drizzling day. Let me know how things turn out.
I didn’t mean to jump, and was replying from dealings with customers. The two wire indoor rated cords my wife stretches to her decorations seem to work fine, much to my consternation.Everyone has there own opinion and I'm just stating mine from past experience with our Christmas decorations. What does surprise me is you jumping all over my reply. Hope you have a good day :thumbsup:
Length of cord between the GFCI device and the lights. Too much cable means the return current takes too long to “return” to the GFCI and it trips.
Well maybe not same electrons, but is essentially looking for same quantity that leaves on one conductor to return at same time on the other conductor.Seriously? Is the GFCI waiting for the same electrons to come back?
Having an EGC in your supply may improve return path characteristics in some instances - but the principle on how GFCI's operate does not require an EGC to function - any leakage to outside the monitored circuit that is over the trip setting will cause them to trip. Since class A GFCI's trip over 4-6 mA it is easy to leak that low of current to ground when you have 120+ volts driving it, especially in wet or damp locations.Everyone has there own opinion and I'm just stating mine from past experience with our Christmas decorations. What does surprise me is you jumping all over my reply. Hope you have a good day :thumbsup:
Any idea where to start looking for a problem with GFCI receptacles tripping when a photo cell controlled contactor comes on?
Are the lights plugged in?
Having an EGC in your supply may improve return path characteristics in some instances - but the principle on how GFCI's operate does not require an EGC to function - any leakage to outside the monitored circuit that is over the trip setting will cause them to trip. Since class A GFCI's trip over 4-6 mA it is easy to leak that low of current to ground when you have 120+ volts driving it, especially in wet or damp locations.
OP could have a cord (with or without EGC) laying in puddle of water, damp foliage, etc that has conductor exposed and that can be where enough leakage is occurring to trip GFCI. That is just one of many possibilities. First reply asking if lights are plugged in is a good place to start.Yes, I know the principle on how a GFCI works, thanks for wanting to help me. Having the EGC greatly improves the chances for the GFCI to trip.
What do you say we all get back to trying to help the OP instead of trying to correct what everyone else has to say? :thumbsup:
OP could have a cord (with or without EGC) laying in puddle of water, damp foliage, etc that has conductor exposed and that can be where enough leakage is occurring to trip GFCI. That is just one of many possibilities. First reply asking if lights are plugged in is a good place to start.