Our mill hangs (2 wire) xmas lights on a chain link fence around our facility, the fence isn't bonded. I have told them not to do this because of the possibility of the fence becoming hot. Which section of the code covers this??
I am not sure which part of the Code covers this situation but there is a mention of the means of attachment of light such as temporary, festoon and decorative lighting must be done by the use of insulating material rated at least to the voltage of the lights.
The use of GFCI's for any outdoor application is also mentioned in the 05 NEC. Following those two rules should make for a safe display.
Does that mean millions of homeowners are in violation when they put lights on their railings?.....
How would that make it safe?Isn't the metal fence connected to metal poles that are buried into the ground?
Isn't the metal fence connected to metal poles that are buried into the ground?
Doesn't mean the fence is bonded. Go with GFCIs and you're fine.
Yes there is metal poles in the ground, but their not bonded back to the panel, earth ground has a high impedance so if the hot wire touches the fence it wouldn't trip the breaker! if the fence was bonded back to the panel it would have a low impedance and the breaker should trip.Isn't the metal fence connected to metal poles that are buried into the ground?
Isn't the metal fence connected to metal poles that are buried into the ground?
Yes there is metal poles in the ground, but their not bonded back to the panel, earth ground has a high impedance so if the hot wire touches the fence it wouldn't trip the breaker! if the fence was bonded back to the panel it would have a low impedance and the breaker should trip.
I'm curious why you made that statement?
That is certainly possible. If for example the resistance of the ground rod to planet Earth was 10 ohms, attaching a 120 volt source to the fence would add 12 amps to the existing load. Depending on how much "normal" load was running at the time, that extra current might be enough to cause the breaker to trip.I have seen a live wire come in contact with a metal fence that did trip the breaker.
I have seen a live wire come in contact with a metal fence that did trip the breaker.
Right. Fences don't shock people . . .But it's not the metal fence that's the danger. It's the energized conductor.
Does that mean millions of homeowners are in violation when they put lights on their railings?
I urinated on a fence once, that SHOCKED me!Right. Fences don't shock people . . .
Right. Fences don't shock people . . .
I got called to one of the prisons we maintain for a report of the fence shocking people. I got there and put meter on fence to ground and I got 97v. After looking around we found that some one had installed new horseshoe stakes. The guy had driven a rod down beside the underground 5200v primary and nicked one of the conductors which was close to the fence. This let the primary "bleed" over to the fence post which made the fence hot. If he would have been 1/4" closer he may not have lived for the horseshoe tournament