Hey everyone, hope everyone is being safe!
-Quick quesiton. Quick backgorund: Recently an estimate for 28 Ductless A/C & Heat Pump combos came across my desk for a Baptist Church in my area. This building is old. This building also has an undersized service. It is 35k sq feet total and has a 400A service.
When sizing the new service I basically used the heat FLA for these units, because in every case it is higher than the A/C, so my question is:
Do I calculate all of them at 100%? In my head I have to, given that they could ALL be cranking ALL the time, as the attached building has the schools, camps, fellowship stuff.
And separating the sanctuary isn't possible because up to 3 days a week, they could be running as well.
Any input is greatly appreciated. Thanks!!
-Shane