Re: church
Jim,
518.4(B) which Bryan mentioned, allows NM to be used in assembly occupancies not required to be of fire-rated construction. I don't know what building code applies where you are, but under the IBC, a church would be classified as an A-3 occupancy. You mention wood framing. Under the IBC an A-3 occupancy of type V-B (nonrated wood frame) construction is allowed to be up to 6,000 square feet. Unless there are other circumstances not mentioned, I would say NM is allowed in the case you mention under the IBC.
[ January 27, 2006, 06:23 PM: Message edited by: eprice ]