I've got a customer requiring all our AC conduit Meyer's hubs be bonded with a minimum #8 copper.
these are 15-30 amp, 120/208 volt circuits in GRC connecting to Nema 4/12 enclosures.
He is citing 250.102(C) specifically and 250.100 generally.
I agree the hubs must be bonded with an EGC, but don't agree with the #8 minimum.
thoughts?