I would like to install a CID2 rated power supply in a Type Z purged enclosure. The idea is to have the power supply power up before the cabinet is purged. Is it OK to have CID2 rated equipment power up on a Type Z purged enclosure before beginning the purge/pressurize process on the enclosure?
It is a CID2 area. I do not see anything specifically forbidding this, and my conscious/judgment is not telling me there is anything wrong with doing this. But it is different than what I have seen in the past, mainly because I am used to Type X purge where this would not be allowed.
I think as long as It is installed and all the wiring to it meet CID2 requirements, then it should be OK.
It is a CID2 area. I do not see anything specifically forbidding this, and my conscious/judgment is not telling me there is anything wrong with doing this. But it is different than what I have seen in the past, mainly because I am used to Type X purge where this would not be allowed.
I think as long as It is installed and all the wiring to it meet CID2 requirements, then it should be OK.