We had to add a 14/2 circuit off a single pole 277V breaker to feed a 200VA transfer that had a 277V input and 120V output. We then added a piece of 14/2 romex from output to coils of 240V straight delta contactors to pull in parking lot lights other day. These were 2 services side by side and totally independent. The 240V had NO GROUND. The 277/480V was typical 4 wire. Firstly, was this code compliant feeding a branch circuit to a transformer to pull in contactors on another service ? Any special rules extra that need to be followed doing this procedure (bonding etc..)