how many cir can i run out to a pool without having to install a sub panel????
AND WHY CANT I FIND IT IN MY BOOK????? LOL
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
The rule is one circuit, or one MWBC to a separate building or structure. In your case, if there is no structure (post counts, building, etc.) then I suppose you can run as many as needed. But if you have several curcuits, a subpanel would make more sense.
 

dcooper

Senior Member
Location
Ma
thats what i was thinking.... i usually do pool houses, but ever since they added 680-2 Corrosive Environment, we have been installing boards outside with disconnects. This one got a little crazy with, a heater, a light, gfci, pump and logic system. I got a little nervous double guessing myself...
TY
 