Longtime reader, first time poster. I hope I can ask a not-specifically-NEC question here.
I have an industrial machine (I follow NFPA79 and UL 508A) requiring the main 480V/3ph disconnect and circuit breaker to be in a separate enclosure from my control panel. It will be directly adjacent, so I can run rigid conduit between them.
I understand the idea: he wants the machine's main electrical enclosure to have no voltage present at all when the disconnect is open and locked.
But under NFPA79, what we've always done is provide a disconnect handle on the enclosure door that doesn't allow the door to be opened unless the disconnect is open or deliberately defeated.
I can provide this "secondary disconnect", but it gives me a bad feeling to have two disconnects next to one another, one of which will leave the other energized.
How do Forum members handle such a "separate disconnect enclosure" requirement ?