Roof Top Unit; reading from unit name plate.
MCA:249A MOCP:250A.
400A C/B as a safety disconnect.
Questions:
1. Maximum Overcurrent Protection device(Inverse time cb)is 250A while Minimum circuit ampacity 249A? Does this make sense? I am trying to contact unit mfgr. if this is right number.
2. 400A c/b mounted on the unit as a safety disconnet. Can you use a higher amp. rating c/b as a safety disconnet while you will have a OCPD at the panel without coordination? Sales rep. told me that this is not sized for trip so it was ok. This doesn't seem right but I can't point out what. Can someone tell me what's wrong.
Thanks.
MCA:249A MOCP:250A.
400A C/B as a safety disconnect.
Questions:
1. Maximum Overcurrent Protection device(Inverse time cb)is 250A while Minimum circuit ampacity 249A? Does this make sense? I am trying to contact unit mfgr. if this is right number.
2. 400A c/b mounted on the unit as a safety disconnet. Can you use a higher amp. rating c/b as a safety disconnet while you will have a OCPD at the panel without coordination? Sales rep. told me that this is not sized for trip so it was ok. This doesn't seem right but I can't point out what. Can someone tell me what's wrong.
Thanks.