buck33k
Senior Member
- Location
- Washington state and North Carolina
An air compressor is turned on daily using a 2 pole 40 amp circuit breaker. HACR
5 HP 230 v.
Nameplate FLA 22.8
table value FLA 28
circuit conductors #8
Is there a safety issue with the existing breaker as far as the initial current imposed on the breaker? Is there another breaker style or rating which would be a better choice?
5 HP 230 v.
Nameplate FLA 22.8
table value FLA 28
circuit conductors #8
Is there a safety issue with the existing breaker as far as the initial current imposed on the breaker? Is there another breaker style or rating which would be a better choice?