bhsrnd
Senior Member
- Location
- Fort Worth, TX
We have two UPS modules, each fed by a 200A breaker on a 480V 3W 3PH panel. A UL regulation we're bound by requires we test these UPS modules each month by disconnecting line-side power for five minutes.
We used to perform this test weekly but ended up burning up the two breakers over time. I know that CB can only take so much on/off and will end up failing over time. Also I feel that peforming this test in this manner put employees at risk for electrocution or other hazard.
For some reason I remember reading somewhere that NEC prohibits the use of a circuit breaker as a switch but cannot locate that verbiage. Although 240.83(D) does afford the use of a CB as a switch for lighting depending on the CB rating (HID or SWD) it does not specifically grant the use of a CB as a switch for anything other than that, nor does it deny.
The electrician we contacted to replace those breakers (at the time this occurred) stated that NEC prohibits the use of a CB as a switch.
Can anyone shed some light on the use of a CB as a switch in this scenario?
We used to perform this test weekly but ended up burning up the two breakers over time. I know that CB can only take so much on/off and will end up failing over time. Also I feel that peforming this test in this manner put employees at risk for electrocution or other hazard.
For some reason I remember reading somewhere that NEC prohibits the use of a circuit breaker as a switch but cannot locate that verbiage. Although 240.83(D) does afford the use of a CB as a switch for lighting depending on the CB rating (HID or SWD) it does not specifically grant the use of a CB as a switch for anything other than that, nor does it deny.
The electrician we contacted to replace those breakers (at the time this occurred) stated that NEC prohibits the use of a CB as a switch.
Can anyone shed some light on the use of a CB as a switch in this scenario?