Question on LVPCB's and accessories / contacts:
For aux. contacts is it a correct statement that if the breaker contacts change state regardless of how [ex.manual operation, shunt trip operation, or tripping function] then the a/b contacts change state respectively. if you were to monitor these points you would only know the contacts changed state but now the why or how.
For Overcurrent Trip Switch / Bell Alarms [with or without lockout], this contact only changes state when the breaker contacts open / trip due to a protective device function [ex. LTPU, LTD, STPU, STD, GFPU, GFD, INST., etc.] and when the overcurrent trip switch changes state so will the aux. contacts because the breaker contacts have changed state. If the breaker is operated via. a shunt trip it would not activate this contact.
so if you were to monitor a aux contact and a bell alarm and the breaker were to "trip" both the trip switch and the aux contacts would change state.
For aux. contacts is it a correct statement that if the breaker contacts change state regardless of how [ex.manual operation, shunt trip operation, or tripping function] then the a/b contacts change state respectively. if you were to monitor these points you would only know the contacts changed state but now the why or how.
For Overcurrent Trip Switch / Bell Alarms [with or without lockout], this contact only changes state when the breaker contacts open / trip due to a protective device function [ex. LTPU, LTD, STPU, STD, GFPU, GFD, INST., etc.] and when the overcurrent trip switch changes state so will the aux. contacts because the breaker contacts have changed state. If the breaker is operated via. a shunt trip it would not activate this contact.
so if you were to monitor a aux contact and a bell alarm and the breaker were to "trip" both the trip switch and the aux contacts would change state.