Re: Circuit Breaker Coordination
Steve -
You are looking at doing a coordination study.
steve66 said:
...Of particular importance, is how do you specify the short time delays and pickups? And how do you know what the practical lower limit of the instantenous setting is?...Steve
You will need to get the trip curves for each CB/fuse. Most of these are available on the manufacturers' internet site.
steve66 said:
...Are there any general rules, such as adding all the motor currents and X times the largest current for the instantenous?...Steve
Probably lots, but I can't think of a one that would give me confidence the system was coordinated and had minimum arcflash. Take a look at the IEEE red book, ch 5. It is a pretty good discussion on trip curves and coordination.
steve66 said:
..I am trying to specify breakers to reduce arc flash without causing false tripping....Steve
From what you are saying, you want the coordination pulled right down tight - the curve each for upstream CB is as tight as you can get it to the downstream load without having nuisance trips.
There are programs like ETAP available for $thousands$. I've got one available and it's complicated and a bear to use for a small study. And I don't use it enough to be any better than slow with it. There are lots of other programs available - I have little experience with any others.
As an alternative, you could get the trip curves for all of the CBs/fuses/overloads and a sheet of Log/Log paper and lay out the motor starting curve, and overlay the trip curves for each upstream device.
Here is an example of one I recently did using 11x17 log/log paper, a straight edge, and colored pens. It was an 800A CB protecting a 1200A feeder and MCC. The question was, "Would the motors start without tripping the feeder CB?
I added up all of the hotel loads (maximum normal running loads including heat and lights) except the largest motor. Threw out any non-coincident loads. Layed that out as the base load. Added the motor starting curve for the largest motor to the base load. Picked out a trip curve (long time/short time settings) for the feeder CB that didn't cross the feeder load. The short time part of the curve is the one that goes around the motor starting bump in load. Just using a hand done sketch got me close enough to give an answer - didn't really need a program.
Here are some generalities from my instructor in a four day coordination class I took 20 years ago: I think they are all still good.
1. If two curves overlap (upstream breaker and downstream CB, they will both trip when you would rather they didn't. Definition of "Coordination" is daylight between the curves.
2. The instaneous on molded case CBs tend to overlap at high short circuit currents. Set the downstream instaneous as low as you can and the upstream as high as you can.
3. Don't believe its coordinated just because the computer program says it is. Get the mfg curves and make sure the program isn't lying to you. (yup - occasionally they lie and sometimes you just fat finger the data entry)
4. MCC faults start phase to ground (unless you are impedance grounded) and the feeder may not trip until it goes phase to phase. A well set ground fault can limit the damage to the phase to ground part.
5. Fuses don't coordinate tightly.
6. You can coordinate anything if you have enough money.
This kind of stuff is generally considered "product of engineering" and all the state law stuff about PE tickets apply - unless you work for the company, and you are not selling the service, and there is no public access and a few other things - but, no news here, from your profile, you already got that.
I'd recommend a good class on coordination. The one I took twenty years ago is still serving me well.
Good luck, you have a tough job.
carl