"I don?t believe that NETA should be viewed and a standard."
NETA ATS and MTS are standards recoginized by ANSI.
"I also question what NETA's basis for MCCB testing is and how it is performed in the field. NEMA AB4 has been around a bit longer than NETA."
I already told you the NETA standard is based on the NEMA AB4
"It is not meant to do a calibration test but is done a 300% of the breakers rated current at which the breaker should trip within a range of time."
Same as NETA
"In addition, contact resistance is not a true indication of the health of a breaker. It may be meaning less or may be an indicator that one should take a closer look."
Thats why NETA (like the NEMA spec) has no set acceptable value for contact resistance, the only spec is if one phase is >50% higher than the lowest phase, then investage further.
"There are 2 things that affect resistance readings
1) The resistance is often measured using very low voltage such with a digital multimeter. "
Not sure who would ever use a mutimeter for contact resistance, not acceptable test per NETA standards. NETA requires at least a 10A output microohmeter or millivolat drop test as you described.
"But being a card carrying NETA member also brings the responsibility of common sense as a skilled professional having training in and understands electrical distributions protection and control systems as well as in safe electrical practices and procedures and knowing that testing is not necessarily a black and white issue."
I could not agree more
You are the one making assumptions that you know more about breaker testing than any of us, how many tests have you actually performed yourself per NEMA AB4? For me, and I would guess Brian too, it is in the thousands of breakers.
One last quote "Do I have to be a NETA member to have access to their MCCB testing procedure to review? "
No you dont you can download it at
www.netaworld.org i suggest you actually read this standard before you say anything else negative about it, following your own advice in your earlier post.