bcorps
Member
- Location
- Evansville, IN
- Occupation
- Engineer
I am looking at a solution to a problem that for some reason is making me feel shady, but I'm not sure if it really is. I did not design the project, but got saddled with the CA on the job when the Engineer who did left the firm.
I have an existing feeder that was served by a 400-amp fusible switch in a switchboard. The fuse values were not available at the time, and the feeder serves three stacked 400-amp panels. in an old building where replacing the feeder would be difficult, to say the least. The demand load from all available information on the panels totaled 278 amps.
So the old switchboard was replaced with a new, circuit breaker switchboard. A standard 400-amp circuit breaker was put in to feed the existing panel stack. No problem, right?
Wrong. The contractor has discovered that the switch is fused at only 300 amps, and the conduit is only 3" EMT.
Shop drawings have been approved, so I'm maybe stuck with the 400-amp breaker. However, it is an adjustable trip, both magnetic and instantaneous. Is it legal to set the instantaneous trip at 300, and the thermal trip at 375, essentially turning it into a 100% rated, 300-amp circuit breaker?
I have an existing feeder that was served by a 400-amp fusible switch in a switchboard. The fuse values were not available at the time, and the feeder serves three stacked 400-amp panels. in an old building where replacing the feeder would be difficult, to say the least. The demand load from all available information on the panels totaled 278 amps.
So the old switchboard was replaced with a new, circuit breaker switchboard. A standard 400-amp circuit breaker was put in to feed the existing panel stack. No problem, right?
Wrong. The contractor has discovered that the switch is fused at only 300 amps, and the conduit is only 3" EMT.
Shop drawings have been approved, so I'm maybe stuck with the 400-amp breaker. However, it is an adjustable trip, both magnetic and instantaneous. Is it legal to set the instantaneous trip at 300, and the thermal trip at 375, essentially turning it into a 100% rated, 300-amp circuit breaker?