Here's the scenario: stand by generator which feeds a Fire pump and also the emerg lighting for the building. Is there a requirement for the generator to have 2 main line circuit breakers? Where in the code?
FYI:I have sized the single generator circuit breaker to be the smallest breaker that will carry between 125% and 250% of the (fire pump full load current + emerg lighting load) and will allow locked rotor current for 20+ seconds.