Circuit Breaker Frame Size

Status
Not open for further replies.

Grouch1980

Senior Member
Location
New York, NY
Hi,
I saw this thread from some time ago:

Post #5 by Jraef explains the frame size of a circuit breaker, where the frame size refers the switch part of the breaker.

What I don't follow is this definition for frame size: The frame size is the designation of the maximum continuous current the breaker can carry.

So if you have a 100 amp circuit breaker, non-continuous rated, the frame size is 80 amps using the definition above? That doesn't make sense.
 
Frame size is not the same as the breaker rating. Frame size is the physical size and configuration of the breaker. A 600 A frame breaker with a 100 A trip will be the same physical size as a 600 A frame breaker with a 600 A trip. Conversely, a 100 A breaker might be a 100 A frame, 225 A frame or a 600 A frame size.
 
Frame size is not the same as the breaker rating. Frame size is the physical size and configuration of the breaker. A 600 A frame breaker with a 100 A trip will be the same physical size as a 600 A frame breaker with a 600 A trip. Conversely, a 100 A breaker might be a 100 A frame, 225 A frame or a 600 A frame size.
I understand that. What I don't understand is the continuous rating definition.
 
Hi,
I saw this thread from some time ago:

Post #5 by Jraef explains the frame size of a circuit breaker, where the frame size refers the switch part of the breaker.

What I don't follow is this definition for frame size: The frame size is the designation of the maximum continuous current the breaker can carry.

So if you have a 100 amp circuit breaker, non-continuous rated, the frame size is 80 amps using the definition above? That doesn't make sense.
A 100 Amp breaker can carry 100 Amps continuously. The problem is the standard terminals and wire attached to them don't allow for enough heat transfer into the wiring so it MIGHT overheat and trip if used at its maximum capacity for an extended period of time.
 
A 100 Amp breaker can carry 100 Amps continuously. The problem is the standard terminals and wire attached to them don't allow for enough heat transfer into the wiring so it MIGHT overheat and trip if used at its maximum capacity for an extended period of time.
I'm not sure that is right. The non continuous rating is due to the real world of breakers being packed with other breakers on either side, and not being in free air.
 
A 100 Amp breaker can carry 100 Amps continuously. The problem is the standard terminals and wire attached to them don't allow for enough heat transfer into the wiring so it MIGHT overheat and trip if used at its maximum capacity for an extended period of time.
What about a 100 amp non-continuous rated breaker?
 
A 100 A breaker in open air can carry 100 A continuously (up to the maximum ambient of its listing). When it's put in an enclosure the continuous rating is reduced due the reduced heat dissipation. Not related to frame size. The exception would be a 100% rated assembly that can carry 100% continuously. This is more related to the enclosure than the breaker.
 
It looks like you got that definition from post number three in the linked thread. I don't think I would agree with that definition and would leave the word continuous out.
I see. And it makes more sense not to use it.

I've actually seen the word 'continuous' used in other places. For example, Elite Software has a charting software where you can graph the TCC curves... they also define the breaker frame size using the word 'continuous'... similar to post #3 in the link.

What I'm gathering here is, the word 'continuous' has a different meaning / context when used to define the frame size. They mean continuous in 'open air', and not in a panel.
 
It looks like you got that definition from post number three in the linked thread. I don't think I would agree with that definition and would leave the word continuous out.
....unless we happen to be talking about a continuous rated breaker. If that makes sense.

If we have two breakers that are exactly the same, except one is continuous rated at 100A, and the other is 80% rated at 100A, I would call both a 100A frame size.

In other words, you would NOT say a continuous rated 100A breaker has a 125 frame size.
 
Frame size has nothing to do with the NEC definition of 'continuous'.
A breaker frame size tells you nothing about its tripping characteristics. Frame size deals with the breaker case physical size and the maximum nominal amps of the contacts and other internal parts. This is important because most manufacturers require same frame size breakers to be mounted across from each other in panelboards and switchboards.
 