For one of my jobs, a circuit breaker in a panelboard will be mounted above 6 ft 7 in.
404.8(A) states that if it used as a switch it's highest position can not be above 6 ft 7in.
My opinion is that it will not be used as a switch because a toggle switch located in another area will provide on/off control for the equipment.
This relates to 404.11 as well.
So, if the circuit breaker is not used as the switch, can it be mounted higher than 6 ft 7 inches?
Thanks
404.8(A) states that if it used as a switch it's highest position can not be above 6 ft 7in.
My opinion is that it will not be used as a switch because a toggle switch located in another area will provide on/off control for the equipment.
This relates to 404.11 as well.
So, if the circuit breaker is not used as the switch, can it be mounted higher than 6 ft 7 inches?