gunny7

Member
There is a 240/120 volt single phase panel board with a 200 amp main circuit breaker incorporated in it in the basement. The homeowner wants to put a 60 amp panel in his new garage where there will be 1-30 amp, 2-20 amp and 2-15 amp circuits. Can this panel in the garage be main lug instead of main breaker? This garage is detached. Thanks Denny
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: circuit breaker panels

Your allowed more than i service panel but they must be grouped together.Double lugs at meter is allowed but the service feeds may need to be upgraded.Dont forget the panel in garage will now be a sub panel and require its own main breaker and ground rod.A main breaker panel will be needed beside the 200 amp also.It will be far cheaper to run a 60 or 100 amp breaker to existing panel and then run to the garage.Depends on if that 200 is needed to carry the house,usually it's not.
Either way the panel outside in garage is a sub panel so split neutrals and grounds.4 wires to garage plus ground rod maybe 2 rods depending on AHJ
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: circuit breaker panels

Denny,
Can this panel in the garage be main lug instead of main breaker? This garage is detached.
225.32 requires that the garage have a means of disconnect. 225.33 permits up to six breakers to be used as the means of disconnect at the garage. As long as the feeder to the garage panel has an overcurrent protective device that has a rating equal to or less than the panel rating a MLO panel at the garage is code compliant.
Don
 

gunny7

Member
Re: circuit breaker panels

Thanks to all. Tthe 200 amp panel in the basement will have a 60 amp breaker for the feed to the garage. Does it have to be a main breaker in the sub-panel or main lug? Specific code?
 

pierre

Senior Member
Re: circuit breaker panels

Don's post has the code references, 225.32, 225.33.
The garage requires a disconnect, but if you have six or less throws (six single or six two pole breakers) than a main disconnect for the panel is not required and a MLO panel is permitted.

Pierre
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: circuit breaker panels

Be carefull if you use ML if it is a 6-12 it won't pass as it could be added to.
For the price of a 60 amp breaker it would be worth having a few extra space for the future
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: circuit breaker panels

Jim,
If it only has six breakers at the time of the inspection, the inspector would be way out of line in red tagging it. The inspector can only inspect what is installed, not something that may be installed in the future. There is nothing in the code section that says you must not be able to install more than six breakers in the panel. It jsut says that you can't have more than six means of disconnect.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: circuit breaker panels

This would be on the same lines of an inspector turning down a 200 amp fusible switch fed with 1/0 and fused at 150 amps because 200's "could" be installed.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: circuit breaker panels

Gunny, see Jim Dungars post in this thread

It's a matter of listing.

Roger
 

hoytmedic

New member
Re: circuit breaker panels

"Either way the panel outside in garage is a sub panel so split neutrals and grounds.4 wires to garage plus ground rod maybe 2 rods depending on AHJ "

I thought under 250 (grounding) additional gnd rods are not required? Ive always understood that gnd rods must be prior to the first discon means?? 250.30 B1 :confused:
 

roger deas

Member
Location
North_Carolina
Re: circuit breaker panels

Actualy this
" so split neutrals and grounds.4 wires to garage plus ground rod maybe 2 rods depending on AHJ "
is agood idea, but may not be true.

If there is no other conductive path to the garage there is no need for an EGC.

The ground rod yes.

See 250.32(B)(2)

Roger

[ December 18, 2003, 08:36 AM: Message edited by: roger deas ]
 