K kriverswaters Member Mar 15, 2013 #1 Is it an NEC violation to use a 3 pole Circuit Breaker for a two pole application, as long as the amperage is correct?
Is it an NEC violation to use a 3 pole Circuit Breaker for a two pole application, as long as the amperage is correct?
7 73cj5 Member Mar 15, 2013 #3 I would defer to manufacturers installation/ ul listings. This would determine NEC compliance.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Mar 15, 2013 #4 73cj5 said: I would defer to manufacturers installation/ ul listings. This would determine NEC compliance. Click to expand... UL Listed breakers have been fully tested for all combinations of poles.
73cj5 said: I would defer to manufacturers installation/ ul listings. This would determine NEC compliance. Click to expand... UL Listed breakers have been fully tested for all combinations of poles.