I need to mount a circuit breaker in the horizontal position. Where in the NEC does it state if the toggle needs to be to the left or to the right when the breaker is in the open or off position.
240.33 Vertical Position. Enclosures for overcurrent devices
shall be mounted in a vertical position unless that is
shown to be impracticable. Circuit breaker enclosures shall be
permitted to be installed horizontally where the circuit breaker
is installed in accordance with 240.81. Listed busway plug-in
units shall be permitted to be mounted in orientations corresponding
to the busway mounting position.
It does not state one way or the other for horizontal.I need to mount a circuit breaker in the horizontal position. Where in the NEC does it state if the toggle needs to be to the left or to the right when the breaker is in the open or off position.
I need to mount a circuit breaker in the horizontal position. Where in the NEC does it state if the toggle needs to be to the left or to the right when the breaker is in the open or off position.
It does not state one way or the other for horizontal.