Circuit breaker rating

Status
Not open for further replies.

E&G

New member
Whats the difference on a 100% rated breaker compared to an 80% rated breaker when sizing the conductor? Use 400 amp c.b.
 
Welcome to the forum.:)

A 100% rated breaker would have any affect on sizing of the circuit conductors. A 100% rated breaker just means that the breaker is designed to run at 100% of its continuous rated load, whereas a non 100% rated breaker is only rated to run at 80% of its continuous rated load.

Chris
 