Does anyone know if series rated combinations apply when the line/load devices are on opposite sides of a transformer?
For example:
at transformer 480V primary/; GE type SFH
at transformer 208V secondary/; GE type TQD
Per the GE's guide "DET008 R12 1211", the TQD is series rated for 22,000A at 240V but I believe the SFH would have to be on the "same side" of the transformer (also applied at 240V).
If there is a specific documentation that discusses this issue that would be helpful (my search results have netted nothing thus far).
For example:
at transformer 480V primary/; GE type SFH
at transformer 208V secondary/; GE type TQD
Per the GE's guide "DET008 R12 1211", the TQD is series rated for 22,000A at 240V but I believe the SFH would have to be on the "same side" of the transformer (also applied at 240V).
If there is a specific documentation that discusses this issue that would be helpful (my search results have netted nothing thus far).