Hello all, i was hoping someone can help with these breaker settings i have. I'm a little confused and i suspect it is labeled incorrectly.
I have a WestingHouse breaker DS-416
Frame: 1600Amp
Rated continuous current 400A (Somebody marked it with a marker on its coverplate) which i suspect is wrong.
The settings the computer spits out is below and this is what it is operating at:
My question is: isn't this breaker sensor setting trips at 600A and not what somebody labeled on it as Rated continuous current 400A? or am i misunderstanding this.
Thank you,
I have a WestingHouse breaker DS-416
Frame: 1600Amp
Rated continuous current 400A (Somebody marked it with a marker on its coverplate) which i suspect is wrong.
The settings the computer spits out is below and this is what it is operating at:
- Frame: 1600A
- Ct Rating 800A
- LT Pick-Up 600A
- LT Delay 4.05
- ST Pick-Up 2400A
- ST Delay .205
- I Pick-Up 4800A
My question is: isn't this breaker sensor setting trips at 600A and not what somebody labeled on it as Rated continuous current 400A? or am i misunderstanding this.
Thank you,