wcorbit721
New User
- Michigan
- Maintenance Manager
I'm trying to understand the correct size panel circuit breaker for a motor connection (air compressor). I have a 20hp air compressor (3-phase AC motor) with a FLC = 30A @460V. Based on 125% overload protection, I will be installing a fused disconnect with 35A fuses. I'm going to feed the disconnect from an adjacent 277/480V Panel and am trying to figure out the correct circuit breaker size. Is table 430.52 of the NEC the correct table for short-circuit/ground-fault protection? If so, what is the correct % factor and why? Thanks!!