steveshow
Member
- Location
- Austin, Tx
- Occupation
- Master Electrician
"For track lighting in other than dwelling units or guest rooms or guest suites of hotels or motels, an additional load of 150 volt amperes shall be included for every 2 ft. of track lighting or fraction thereof. Where multi-circuit track lighting is installed, the load shall be considered to be divided equally between the track circuits. Exception: If the track lighting is supplied through a device that limits the current to the track, the load shall be permitted to be calculated based on the rating of the device used to limit the current."
I have encountered several electrical designers/ P.E.s that show hundreds of feet of track lighting, with no current limiter listed on the fixture schedule or called out in the manufacturer cut sheets. They argue that the circuit breaker meets the exception of being a current limiting device. My first argument is that a 20 amp (or any amp rating, for that matter) circuit breaker will not protect the track from overload. None of them can wrap their heads around the fact that human nature of "non-qualified personnel" is to clip more and more track heads on a track, until the desired lighting level is attained, potentially overloading the track. There hasn't been a valid argument against this. My second argument is if the circuit breaker is the current limiting device, why is the exception mention at all? The circuit would be covered by 240.4. (It's not, because 240.4 addresses conductors, not devices, but again, this point is lost on them. Any thoughts? I have not been able to find any discussion on this topic, either here on the internet in general.
I have encountered several electrical designers/ P.E.s that show hundreds of feet of track lighting, with no current limiter listed on the fixture schedule or called out in the manufacturer cut sheets. They argue that the circuit breaker meets the exception of being a current limiting device. My first argument is that a 20 amp (or any amp rating, for that matter) circuit breaker will not protect the track from overload. None of them can wrap their heads around the fact that human nature of "non-qualified personnel" is to clip more and more track heads on a track, until the desired lighting level is attained, potentially overloading the track. There hasn't been a valid argument against this. My second argument is if the circuit breaker is the current limiting device, why is the exception mention at all? The circuit would be covered by 240.4. (It's not, because 240.4 addresses conductors, not devices, but again, this point is lost on them. Any thoughts? I have not been able to find any discussion on this topic, either here on the internet in general.