Hi Everyone - I have a roof top generator with a 4000A 3P LSIG output breaker. This is being installed as a separately derived system.
The output of the generator is landing in a switchboard where we are using circuit breakers to transfer normal to optional stand by power automatically. From my understanding (please correct me if I'm wrong) a system bonding jumper needs to connect the generator neutral terminal to the frame of the generator, then a grounding electrode conductor needs to connect the generator frame to the main building ground bar.
For the neutral conductor, I normally just provide a 4 pole ATS so it can disconnect from the system, since I'm using power logic and breakers for power transfer, how does the neutral disconnect from the generator (under normal conditions) using breakers within the gear? I can't really wrap my head around it and feel like I'm missing a core piece of knowledge here.
The output of the generator is landing in a switchboard where we are using circuit breakers to transfer normal to optional stand by power automatically. From my understanding (please correct me if I'm wrong) a system bonding jumper needs to connect the generator neutral terminal to the frame of the generator, then a grounding electrode conductor needs to connect the generator frame to the main building ground bar.
For the neutral conductor, I normally just provide a 4 pole ATS so it can disconnect from the system, since I'm using power logic and breakers for power transfer, how does the neutral disconnect from the generator (under normal conditions) using breakers within the gear? I can't really wrap my head around it and feel like I'm missing a core piece of knowledge here.