marcus1 said:can some one point me in the right direction . question: can a 3 phase breaker be the disconnect means for a single phase load can't find in code
yursparky said:Question is: Is it listed to be used as a single phase disconnect?
enosez said:but are you asking if a three pole breaker can be wired using only one of its legs.
It now says that multi phase circuits (a, b, c phase with one neutral) all ungrounded conductors must be turned off by the same device. Not in those words though.. So, it seems that a 3 pole breaker will be the ONLY way to protect the hot's on the same neutral. I hope this make some sense??
charlie b said:It's not in the code. That is usually enough of a reason to say that it is allowed. But why would anyone want to?
Welcome to the forum.
A UL 489 listed breaker has been tested for 1, 2, and 3 pole operation.
billsnuff said:but wouldn't you loose all three if one faulted vs. three singles, you would loose one, but have to shut off all three for repair?
edit spelling
nec2008 said:210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.
FPN: A 3-phase, 4-wire, wye-connected power system used to supply power to nonlinear loads may necessitate that the power system design allow for the possibility of high harmonic currents on the neutral conductor.
(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
FPN: See 300.13(B) for continuity of grounded conductor on multiwire circuits.
(D) Grouping. The ungrounded and grounded conductors of each multiwire branch circuit shall be grouped by wire ties or similar means in at least one location within the panelboard or other point of origination.
Exception: The requirement for grouping shall not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious.