circuit breakers

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
It is allowed if the is listed for two conductors. See 110.14(A)

Roger
 
SQD typically has the means for 2 conductor termination:
07036.jpg





There are other manufacturers as well who do. The best way to identify which CBers do or do not permit more than one conductor is to read the instructions.
If you are not sure, you could alway splice the conductors in the panel enclosure and then terminate the single conductor to the CBer.
 